Default Nat gas line size calculations etc.

Hey fellas.

Just moved into a new residence. Among many renovations wife would love to opt for gas range..... Oh joy.
I like to play safe and hold 2 trades tickets. With that said id love some assistance.

Main line is 3/4 npt and is branching off at various points to 1/2 npt.
Furthest point of line runs to the garage heater.....
@ 38 ft 3/4 npt - 45k btu ( last 8 ft reduced down to 1/2 npt )
@ 10ft 3/4 npt - 88k btu furnace ( last 1 ft reduced to down to 1/2 npt )
@ 10ft 3/4 npt - 45k btu HWT ( last 6 ft reduced to down to 1/2 npt )
@ 18 ft 3/4 npt - 50k btu PROPOSED NEW GAS RANGE ( reduced to 1 or 2 ft 1/2 npt ? )
The last run to the range is all ready there from a previous run for a nat gas fireplace. Its just capped off ready to accept some black pipe or csst.


I have lots of online literature regarding gas line sizing but would love to hear from a veteran who does alberta gas fitting. What chart or calculations do you use to figure out this max btu the 3/4 npt line can handle at these distances.


I appreciate the help.
Reply With Quote
  #2  
Old 04-02-2019, 01:00 PM
Dewey Cox's Avatar
Dewey Cox Dewey Cox is offline
 
Join Date: Jan 2012
Location: 204
Posts: 5,660
Default

All the relevant charts are in the gas codebook.
__________________
I don't think our taxes should be this high.
Reply With Quote
  #3  
Old 04-02-2019, 01:53 PM
Robins36's Avatar
Robins36 Robins36 is offline
 
Join Date: Apr 2015
Location: Leduc
Posts: 233
Default

Need the total distance from the meter to the furthest fixture.
Pm me your email and I will send you the screen shot from the code book.

Daryl
Reply With Quote
  #4  
Old 04-02-2019, 04:12 PM
hawken's Avatar
hawken hawken is offline
 
Join Date: Jun 2007
Location: Calgary
Posts: 561
Default

Total distance from the meter to the furthest fixture for 3/4"
Up to 30' = 262 Mbh
40' = 224 Mbh
50' = 199 Mbh
60' = 180 Mbh

You have 228 Mbh
You will have to tie the new line in within 2' of the meter.
Also, any gas work done requires a permit.
Reply With Quote
  #5  
Old 04-02-2019, 07:43 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,439
Default

Hawken has it. To add to his mention of the permit, I know that Calgary does not allow homeowners to pull gas permits. Homeowner plumbing permits yes, but gas work needs a licensed gasfitter to perform it legally.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #6  
Old 04-02-2019, 08:11 PM
VooDooMan's Avatar
VooDooMan VooDooMan is offline
 
Join Date: Nov 2012
Location: Edmonton
Posts: 54
Default

Thanks for all the replies.

Hawken. You added up all my btus to come to 228. Mbh is thousands of btu per hour. Correct ?
From my digging I came to the same conclusion. Ill have to T off from the meter.
Can you run csst from the meter or any thing outdoors / meter connection has to be black pipe ?

I can indeed pull my own permit according to https://www.edmonton.ca/programs_ser...s-permits.aspx

What does thy say for a new run from the meter to my range. 1/2 npt ?
What is the actual mbh for 1/2 npt at 20 30 40 ft?

Thanks again.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 05:36 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.